Hi,
thanks in advance for the help.....I know this is a difficult question to answer. I have read through the forums and have not seen a direct answer.
I have purchased a used glycol unit- the pump puts out 49 PSI at 50 GPM- there is a 70 gallon res.
I will be controlling 4 jackets with this unit.
I do not want to over pressurize my jackets.
I will install a bypass etc.
is there a way I can that I can reduce the pressure by increasing the header size.....say go with a 2 inch header to reduce pressure.
Is there a calculation for this?
I would like to avoid a vfd or pump change if at all possible....but if that's what it takes-ill do either.
thanks a ton in advance