    hello forum-

    sorry to re-hash an old topic, but we are having trouble affording some of the nicer piping options for glycol, and are curious as to what everyone is using.

    we are starting a new micro up here in seattle, usa, called odin brewing. have scoured this forum and it's great to see everyone sharing their experience and hard-fought knowledge they've gained.

    i have been involved in a start-up build before, but it was in ireland and i can't remember the types of piping we used. we are planning on using sch.80 pvc or abs, un-insulated, for our mains, but cannot decide what to use for piping the jackets....1.5" mains and 3/4" jacket lines...i have heard nitrile, radiator hose, copper, pex, etc...just wondering what people use that is reliable but still affordable...(prob not copper due to tight budget)...

    any help or suggestions would be great. i read braided hose somewhere and was wondering which type of braided hose exactly? and does the pex withstand the -27f temps?

    thanks again for any help.

    cheers,

    brian

  • #2
    Please consider the value of what a leak costs: Fermenter temp out of control... likely dump the brew. Nine f*ing hundred dollars of glycol to refill the glycol tank..."ideally" when the refrigeration supply place is open.
    Sucks. Been there.
    This separate from the efficiency aspect.
    I have PVC and hose. Just be sure connections are snug and safe. I understand ABS is more durable than PVC at low temps.
    Do you feel lucky?
    Last edited by Moonlight; 08-20-2009, 03:09 AM.

    Comment


    • #3
      I used CPVC at my last brewery. It worked well, was easy to install and available locally at the big home stores. I used 3/4 and insulated it with split foam insulation. We were a 25 bbls setup and it is probably a little undersized so I would recommend bigger pipe.

      Mike
      Mike Pensinger
      General Manager/Brewmaster
      Parkway Brewing Company
      Salem, VA

      Comment


      • #4
        Oh yeah... I spoke with the Wirsbo PEX people and they assured me that I could not get their PEX tubing cold enough to cause and issue. We used PEX to wrap a plastic tank to make a CLT at my current brewery and it works pretty well (Plastic to plastic doesn't conduct heat so great).

        Mike
        Mike Pensinger
        General Manager/Brewmaster
        Parkway Brewing Company
        Salem, VA

        Comment


        • #5
          plumber

          As I write this im waiting for a plumber to get here to fix leaks (yes plural) in my pvc glycol pipes. Leaks are right by the tank so I assume its from expansion during cleaning with hot coustic. I never had a problem with copper in over 10 years other than learning how to solder to replace a solinoid. G. Fisher's ABS is sweet, but the cost is huge, 27$/ft for the insulated I think.
          And for size 2" main w/ 1" to tanks is min. I would go with. Flow baby, flow!
          Last edited by Ted Briggs; 08-20-2009, 10:56 AM.
          Brewmaster, Minocqua Brewing Company
          tbriggs@minocquabrewingcompany.com
          "Your results may vary"

          Comment


          • #6
            Metal to Plastic Fittings

            We used to have issues of PVC leaks right at the tank because of thermal expansion. We added these fittings and haven't had any issues:

            McMaster-Carr is the complete source for your plant with over 595,000 products. 98% of products ordered ship from stock and deliver same or next day.





            Cheers,

            dave

            Comment


            • #7
              Hi,
              A correction regarding the price for COOL-FIT ABS Plus pipe (pre-insulated). For 1 1/2" pipe it is about 13.42$ /ft and for 2" pipe it is about 16.43$ /ft.
              If you go with the un-insulated COOL-FIT ABS your 1 1/2" pipe will cost you about 2.61$ /ft and the 2" pipe is about 4.62$ /ft. As a comparasion list price for 1 1/2" Copper pipe type M is about 10.82$ and 2" is about 17.06$

              As said many times before the lowest limit for PVC or CPVC is 32F and some producers even say 40F. Some producers also don't allow propylene glycol in their PVC & CPVC piping.
              Lowest limit for COOL-FIT ABS is -40F and for COOL-FIT ABS Plus -58F. Pressure rating 150 psi (174 psi below 50F).

              Best Regards,

              Dan Strömberg

              Market Segment Manager

              Cooling & Refrigeration



              GF Piping Systems

              Georg Fischer LLC

              2882 Dow Avenue, Tustin, CA, 92780

              Tel. (714) 368-4196, Fax. (714) 368-4197

              Cellular. (951) 642 2339

              dan.stromberg@georgfischer.com



              Comment


              • #8
                Thanks for the update. My memory was from a MBAA meeting a few years back At Dogfish Head. Guess you got the price lower or I had too many 90Mins IPA's--lol
                The plumber is suggesting Pex to the tank- I see beermkr used that. hopfully it will take care of the thermal issue and any possible pipe hammer from solinods opening and closing.
                Im also going to get him to put air bleeds on each tank, on the high point of the exit pipe too while the system is down. Might solve one tank cooling to 35while others will only get to 38......
                Brewmaster, Minocqua Brewing Company
                tbriggs@minocquabrewingcompany.com
                "Your results may vary"

                Comment


                • #9
                  I always wondered how folks were complaining about PVC breakage. Our headers are PVC and the drops to the tanks are all copper down to a dielectric union. I bet it is the heating a cooling at the tank on the drops that does it.
                  Joel Halbleib
                  Partner / Zymurgist
                  Hive and Barrel Meadery
                  6302 Old La Grange Rd
                  Crestwood, KY
                  www.hiveandbarrel.com

                  Comment


                  • #10
                    great - thanks for the suggestions - we have 30bbl tanks, 7 of them, so gonna increase the pipe sizes....found pvc80 at 1.40 a foot, and dan's abs is 2.62 a foot...hmmm...gotta try to convince the boss man on this one...also thinking of doing the pex to the tanks, for flexibility...still no one ever used braided hose or radiator hose? not gonna do any pvc from mains to tanks...seem to be too many leaky stories here...

                    thanks again,

                    cheers,
                    brian

                    Comment


                    • #11
                      Remember the labor is essentially the same, I think for $1 a foot price difference, the ABS is a smart investment choice.

                      Although not as common in breweries, it is real common to see wineries using flexible hose from their main glycol headers down to the jacket inlet connections.

                      The hoses we have seen utilized with success and offer are a Nitril hose rated for applications up to 250 PSI and from -20 F to 190 F. These are classified as a "premium multipurpose hose" by the hose manufacturer. Wineries are often moving their vessels and will also utilize quick connect check valves to facilitate this. You can order in any length with any connection, typically female or male pipe thread connections.

                      I'd be happy to swing by and meet with you and help explain some different options that I am familiar with. We are located about 25 minutes south of Seattle.

                      Thanks

                      Jim VanderGiessen
                      Pro Refrigeration Inc.

                      Comment


                      • #12
                        M.G. Newell has installed unpolished stainless tubing and have had great success. We certainly recommend insulating the lines as you do not want to lose temperature or have a lot of condensate. The PVC, while cost savings up front, will not last and give you headaches in the long run.
                        Gray E. Sherrill
                        M.G. Newell Corporation
                        800.334.0231 office
                        336.404.1375 cell

                        Comment


                        • #13
                          Hi,
                          One more note that could be of interest.
                          The inside diameter of a 1 1/2" schedule 80 PVC pipe is 37.5 mm (1.476") compared to the inside diameter of a 1 1/2" COOL-FIT ABS pipe that is 44.0 mm (1.732"). The inside diameter of a 1 1/4" COOL-FIT ABS pipe is 35.2 mm (1.386"). So sometimes you can go down one pipe size when you use the COOL-FIT or you get more flow out to the tanks.

                          Regards

                          Dan