    Tons = BTU

    I am trying to size a chiller system for a 4bbl brew system. I have one 4bbl fermentor and 2 4bbl conditioning / serving tanks (jacketed) I may add another fermentor and brite later on but for this discussion I will start here. I have been told I will need at least 3,000 BTU per tank and have seen some models rated in TONS. Other places rate it by the compressor size like 2 hp. Can someone tell me how these all equate? Am I on the right track with my size? Also what size glycol bath do I need? Thanks

  2. #2
    Join Date
    Jul 2005
    Location
    Auburn, WA
    Posts
    189
    I ran a cooling load estimate based on a 4 Bbl FV being crash cooled from fermentation temp (68 F) to conditioning temp (34 F) in 24 hours and 2 Ea 4 Bbl Conditioning tanks holding at 34 F. The estimated cooling load is about 3,000 BTU/HR.

    You will want a chiller system rated at least at 3,000 BTU/HR cooling capacity at 28 F Glycol and 90 F Ambient. This is roughly something in the 1/2 HP Range.

    1 ton of refrigeration is 12,000 BTU/HR.

    Our systems currently start at 2 HP, rated at about 15,000 BTU/HR. Quite a bit oversized for this duty, unless you plan to expand and add tanks in the near future.

    Hope this helps,

    Jim
    Pro Refrigeration.com

  3. #3
    Join Date
    Feb 2008
    Location
    San Diego
    Posts
    38

    BTUs

    Thank you Jim, that helps me alot.
    One other question, What size glycol bath (reserve) do you think I will need ?
    I see alot of chillers for longline draft systems and the Micromatic MMPP 4302 perhaps could work? I am in India building this thing and will be shipping it to Kiev to install. Micromatic Asia will not even return my calls nor will the Russia Rep. I will have a few weeks in Germany to deal with this but I have an option to have it custom built in Germany as we eventually need dozens of them. So thinking now weather I should waste more time dealing with Micromatic or start fresh in a country that knows what a Brewery is.
    Thanks,
    Vance

  4. #4
    Join Date
    Jul 2005
    Location
    Auburn, WA
    Posts
    189
    What is your budget for this unit, would you be interested in a quote for a system imported from the United States?

    We just manufactured a small 1/2 HP Chiller system rated at apprx 6,000 BTU/HR- this was built for a tradeshow display. We are considering adding this to our product line. This system is supplied with a 5 gallon reservoir. We will be testing this in a brewery following the tradeshow.

    With our ChilStar Series (2 HP to 7.5 HP) operate with a 22 gallon reservoir, our larger systems are supplied with reservoirs from 100 gallons up to 2,000 Gallons.

    Good luck in your venture.

    Jim
    www.prochiller.com

  5. #5
    Join Date
    Feb 2008
    Location
    San Diego
    Posts
    38

    Budget

    To be honest I don't know what my budget is but I I know my bosses are cheap (aren't they all?). Multiple units are will be needed and maintaining and servicing them all over the world plays into a factor of x=1 quality source from 1location Y=a knockoff from ? &Z sourcing our refridgeration in each location. My bosses are willing to listen to any informed suggestions I make but we are talking about 20+ countries here. What do you suggest? The mantra is "do it right" but we we do have costs and realites to deal with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •