    This is the Loop designed for my brewery
    10 Bbl FV and BT's, 4 of ea. with 4 - 2 Bbl Unitanks and a drop for the HX
    2 1/2" header and 1" drops
    Designed to handle full BT's, as we are using them as serving tanks, and have the capacity to add 4 more brites if needed
    Have i forgotten anything?

    Click image for larger version

Name:	image1 (1).jpg
Views:	1
Size:	90.3 KB
ID:	194707

  • #2
    Hi,
    This is how I would lay it out to use less piping.
    The supply can be built out when you expand but you need to put in the return pipe allready from the beginning. I would also then suggest to put in the reduced tees and manual valves for future tanks (and also for future bypass).
    I would put a bypass valve just before the valve for future supply. That one will be closed later on when the future supply is in.
    How many jackets do each FV and bbt have?
    Do you know the recommended flow for each jacket (or tank)?
    What is the max flow from your chiller?

    Click image for larger version

Name:	3 Bridges Brewing.jpg
Views:	1
Size:	86.6 KB
ID:	191299
    Cheers!

    Dan

    Dan Strömberg
    Cooling Market Segment Manager
    Georg Fischer LLC
    Phone: +1 714 368 4196
    Fax: +1 714 368 4197
    Mobile: +1 951 642 2339
    Dan.Stromberg@georgfischer.com

    GF Piping Systems
    9271 Jeronimo Rd., Irvine, CA. 92618
    United States
    GF Piping Systems is the leading flow solutions provider across the world. We enable the safe and sustainable transport of fluids. Our business is driven by maintaining industry-leading sustainability levels, innovating through digitally enabled solutions, and investing in a culture built on performance, learning, and caring.

    Comment


    • #3
      My main concern would be that you are in FL and it looks like you are using a glycol stage on your HEX. You can make that work, but with the groundwater temperatures in the summer here, you will likely be much happier in the long run if you can find a way to put a dedicated cold liquor tank in your brewery.

      Comment


      • #4
        Sizing Etc.

        You may not need 2-1/2" mains for that small of a system.
        Do I understand your FV's are 10 bbl only?
        We run in the range of 600 bbl diversified fermentation load on 2" and its more than enough size wise.
        Manual bypass valves are typically not necessary on this kind of loop as shown.
        Chillers that are set up for Brewery usage have bypass regulator controls built in with the process pump discharge.
        THE CLT suggestion is a good one with an HX that allows for 2 stages of cooling input.
        Last edited by Starcat; 02-08-2017, 06:36 AM.
        Warren Turner
        Industrial Engineering Technician
        HVACR-Electrical Systems Specialist
        Moab Brewery
        The Thought Police are Attempting to Suppress Free Speech and Sugar coat everything. This is both Cowardice and Treason given to their own kind.