Howdy,
We've got a Columbia MPH60 and its a real power house of a boiler, probably oversized for our application, 1 30BBL kettle (bottom and side) 1 90BBL HLT (side only), and 1 30BBL MT (side only)...I can provide exact heat transfer area if someone out there wants to get real technical...but I'm assuming at over 2 million btu's that we're fine with capacity.
Now, I am having a sluggish time getting up to boil. I am assuming that the standard temp rise is 1ºC per minute...we're getting about 0.10ºC per minute.
The pressure in the boiler is cut off at 1 BARG (14.7psi) and then it is unregulated into our process vessels.
Now, from a few previous breweries working experience, the boiler built up pressures to 30-45 psi and then there were pressure regulating valves before the vessels that were asking demand. These boilers were also termed "low pressure boilers" even though they were set at building up pressures above 14.7.
My argument to my bosses (and perhaps incorrect) is that the vessels will not get 14.7psi very quickly if the boiler is only producing 14.7psi, loss in pipelines, etc...
Then the contractor tells me that it is code and that we are only allowed to use low pressure steam boiler and therefore boiler cannot be set above 14.7psi. My reply is that the terminology of a "low pressure boiler" has to do with the size/capacity of the internal coil for that classification...ie a low pressure boiler can still produce 30-45 psi so that we can have adequate supply of 14.7 psi at our vessels.
So, i'd like to increase the set point on the boiler up to say 30psi (and change the safety valves to allow this), and then have pressure reducing/regulating valves at the vessels set at 14.7psi.
If this is a faulty logic, then my other possible explanations are that there is no bypass on the kettle steam piping and there may be water logged in the jacket thereby reducing the heat transfer surface and causing long times to reach boil.
Last possible reason is that there is no moisture separator in the supply line so the steam being supplied to the vessels is "wet" and therefore less steam heating capacity.
The vessels are CIPed regularly and no visible scale or physical reason why jackets should be underperforming. We've got the right boiler. I think the piping is ill-conceived or the set point needs to be adjusted.
Any tips or suggestions or reality check would be appreciated.
Thanks!
We've got a Columbia MPH60 and its a real power house of a boiler, probably oversized for our application, 1 30BBL kettle (bottom and side) 1 90BBL HLT (side only), and 1 30BBL MT (side only)...I can provide exact heat transfer area if someone out there wants to get real technical...but I'm assuming at over 2 million btu's that we're fine with capacity.
Now, I am having a sluggish time getting up to boil. I am assuming that the standard temp rise is 1ºC per minute...we're getting about 0.10ºC per minute.
The pressure in the boiler is cut off at 1 BARG (14.7psi) and then it is unregulated into our process vessels.
Now, from a few previous breweries working experience, the boiler built up pressures to 30-45 psi and then there were pressure regulating valves before the vessels that were asking demand. These boilers were also termed "low pressure boilers" even though they were set at building up pressures above 14.7.
My argument to my bosses (and perhaps incorrect) is that the vessels will not get 14.7psi very quickly if the boiler is only producing 14.7psi, loss in pipelines, etc...
Then the contractor tells me that it is code and that we are only allowed to use low pressure steam boiler and therefore boiler cannot be set above 14.7psi. My reply is that the terminology of a "low pressure boiler" has to do with the size/capacity of the internal coil for that classification...ie a low pressure boiler can still produce 30-45 psi so that we can have adequate supply of 14.7 psi at our vessels.
So, i'd like to increase the set point on the boiler up to say 30psi (and change the safety valves to allow this), and then have pressure reducing/regulating valves at the vessels set at 14.7psi.
If this is a faulty logic, then my other possible explanations are that there is no bypass on the kettle steam piping and there may be water logged in the jacket thereby reducing the heat transfer surface and causing long times to reach boil.
Last possible reason is that there is no moisture separator in the supply line so the steam being supplied to the vessels is "wet" and therefore less steam heating capacity.
The vessels are CIPed regularly and no visible scale or physical reason why jackets should be underperforming. We've got the right boiler. I think the piping is ill-conceived or the set point needs to be adjusted.
Any tips or suggestions or reality check would be appreciated.
Thanks!