  • Alpha King
    replied
    You will use approx. 320 gal of 36 degree CL to knock out in 50 minutes if you have a heat X that is sized for a 10 bbl batch. I would recommend a 15 bbl CLT for cushion and if you plan to knock out down to lager temps.
    Cheers, Marc Martin (Northwest Brewery Advisors)

    Leave a comment:


  • barleyfreak
    replied
    We are on a 7bbl brewhouse and though I do not have a dedicated CLT, I do use an empty FV as a CLT whenever I have one. FYI, for me to cool a 7bbl batch to 64 degrees pitch temp with 34 degree water I use about 230 gallons. To get to lager pitch temp of 51 degrees I need about 340 gallons. My HX came with my Premier System so I reckon it sized for a 7bbl BH.

    Dave

    Leave a comment:


  • craftkettlebrew
    replied
    A properly designed heat exchanger should utilize about 1.3 gallons of water to 1.0 gallon of wort to chill within ~10 degrees of the water temperature (the target wort temperature being about 50 deg F), so you'll need a 10 BBL CLT at minimum, although that is cutting it close. We typically size a CLT to be 2X the brewhouse size, so a 15 BBL CLT would be appropriate and ensure that you don't run out of cold water. Email me and I can get a quote together for you.
    _
    JEREMY KING
    Brewery Design Consultant, Experienced Commercial Brewer
    jeremy.king@craftkettle.com​ | d 504.930.4462 (schedule a call)

    CRAFT KETTLE BREWING EQUIPMENT
    1652 Religious St New Orleans, LA​ | p 855.953.8853
    www.craftkettle.com
    @craftkettle

    Leave a comment:


  • LastFlight
    started a topic Cooling Wort With a CLT

    Cooling Wort With a CLT

    Hello all, we're opening a 7 bbl brewery in Missouri in the next few months. Our ground water temp in the summer is about 78F (25C) so we're trying to figure a way to ensure we can cool down to pitching temps. We're currently planning on using a CLT, which will be about 38F (3C). Our heat exchanger is going to be designed for a 10 bbl system. Any ideas on how large my CLT needs to be? 500 gallons was my best guess.