    Quote Originally Posted by augiedoggy View Post
    Thanks, my question was more or less if there were a lot of breweries out there already using non ul listed panels since I built my own (using UL listed components and built to code) but I don't really want to send it out for the union to bless it considering costs if I don't have to.
    If you end up being required by your local jurisdiction to get the panel labeled, you might check to see if they'll accept ETL labeling in lieu of UL. They may be much cheaper for this. As far as the actual code goes, it doesn't have to be UL, it just has to be a "recognized testing laboratory" and the NFPA has a list of what they consider to be recognized. Your jurisdiction should accept ETL, but I've found some inspectors can be jerks.

    Regards,
    Mike Sharp

  2. #17
    Join Date
    Oct 2016
    Location
    Jameson, SK, Canada
    Posts
    164
    Quote Originally Posted by augiedoggy View Post
    Thanks, my question was more or less if there were a lot of breweries out there already using non ul listed panels since I built my own (using UL listed components and built to code) but I don't really want to send it out for the union to bless it considering costs if I don't have to.
    That depends on the knowledge and thoroughness of your local inspector, and your tolerance for risk.

    JR

  3. #18
    Join Date
    Oct 2017
    Location
    western , NY
    Posts
    122
    Nevermind.
    Last edited by augiedoggy; 04-01-2018 at 11:14 AM.

  4. #19
    Join Date
    Oct 2016
    Location
    Jameson, SK, Canada
    Posts
    164
    Quote Originally Posted by augiedoggy View Post
    Nevermind.
    My apologies. If the realities of your question upset you, try asking somewhere else.

    I know that the electrical inspectors in Ontario have cracked down on non-uL panels. Other jurisdictions have seen people getting away with it.

    Again, sorry that I/we can’t predict the future and/or read the mind of your local inspector.

    Good luck.

  5. #20
    Join Date
    Oct 2017
    Location
    western , NY
    Posts
    122
    Quote Originally Posted by Jer View Post
    My apologies. If the realities of your question upset you, try asking somewhere else.

    I know that the electrical inspectors in Ontario have cracked down on non-uL panels. Other jurisdictions have seen people getting away with it.

    Again, sorry that I/we can’t predict the future and/or read the mind of your local inspector.

    Good luck.
    It wasnt the "Realities or my question you gave that upset me.. It was the assumption that since even though I stated my panel was built to NEC code using all ul recognized components, that it was unsafe. I do not see the difference from the other electrical panels and work done onsite that he is allowed to deem ok due to certified components and correct installation. Itsd frustrating when you know having the UL inspect it will cost multiple times what the panel cost to build
    Last edited by augiedoggy; 09-26-2018 at 02:04 PM.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Meeting with county tomorrow to discuss starting a nano brewery
    By jbunton in forum Nano Systems Q&A (Sponsored by Sungood Machinery)
    Replies: 2
    Last Post: 10-14-2016, 05:35 PM
  2. Starting a Micro/nano
    By ironman1997 in forum Nano Systems Q&A (Sponsored by Sungood Machinery)
    Replies: 14
    Last Post: 07-09-2016, 06:53 PM
  3. Starting out
    By DrinkGoodBeer in forum General R&B Discussions (Available for sponsorship)
    Replies: 9
    Last Post: 12-28-2010, 11:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •