I will be needing a glycol chiller for a 7bbl brite beer tank and want to know what the correct size chiller is. Is there a standard equation to figure this out.
Announcement
Collapse
No announcement yet.
Glycol Chiller Sizing?
Collapse
X
-
Contact the folks at Pro Refrigeration, http://www.prorefrigeration.com/redesign.html. They can tell you everything you need to know about chilling.
Prost!
DaveGlacier Brewing Company
406-883-2595
info@glacierbrewing.com
"who said what now?"
-
Brite Tank Cooling Load
There are a few factors needed to calculate this load, such as the storage room temperature and the beer holding temperature.
Is this the only load you will be requiring a chiller system for, the duty should be very small.
Please call me when convenient, we would be happy to calculate this up for you.
Thanks,
Jim
Pro Refrigeration Inc
800-845-7781 ext 203
Comment
-
Open calculation
Hi Jim,
Could you post your calculations here on the thread. There is a lot of interest for "cooling volumes" and I am sure there are a lot of people out there like me who would like to learn the basics of it.
I hope you don't mind.
Thanks
BelgianBrewer
Last edited by BelgianBrewer; 04-05-2008, 01:26 AM.
Comment
-
Understanding refridgeration thread
I found this thread in May while researching a new chiller:
I ultimately purchased a 35 HP unit from ProBrewer sponsor Pro refridgeration. Give Jim a call.Cheers & I'm out!
David R. Pierce
NABC & Bank Street Brewhouse
POB 343
New Albany, IN 47151
Comment
-
load calculations
Originally posted by BelgianBrewerHi Jim,
Could you post your calculations here on the thread. There is a lot of interest for "cooling volumes" and I am sure there are a lot of people out there like me who would like to learn the basics of it.
I hope you don't mind.
Thanks
For PULL DOWN LOADS (can be used for Fermenter Pull Down or Cold Liquor calculation)
Total pounds of product you are cooling in an hour, multiplied by the degrees temperature (F) that you are cooling.
Example:
7 Bbls = 217 Gallons = approx. 1900 lbs
1900 lbs X cooling 42 F (75F to 33F) = 79,800 BTU
79,800 BTU / 6 hours = 13,300 BTU/HR
For ACTIVE FERMENTATION
Total Barrels in Active Fermentation X 15 Bricks per BBL X 280 BTU per Brick / length of active fermentation. We use a default of 72 hours, understanding that many beers will ferment longer, but a majority of the heat gain is going occur in that first 72 hour period.
Example:
300 Bbls X 15 Bricks = 4500
4500 X 280 BTU/Brick = 1260000
1260000 / 72 HR = 17,500 BTU/HR
Some people specify and size chiller systems simply based on the annual brewery production, and they might be right. Our approach is to size for a “real” load condition. We take a snapshot of that facility during a normal, to high, load condition. Adding up the estimated cooling requirements based on what state each vessel is in. We then factor for heat/cooling loss due to room temperatures, line loss, insulation, pumps motors, etc. etc. This is also used to estimate the glycol flow requirements for each brewery.
Please contact me directly if you would like us to provide a load estimate. I can send over a survey to complete- or you can call and we can fill out over the phone.
I hope this is helpful.
Good luck,
Jim
jimvgjr@prorefrigeration.com
Pro Refrigeration Inc.
800-845-7781 ext 203
Comment